UBZNZ wrote:
Interesting read .
Personally I wouldnt use one of those Radarc battery isolates with a winch.
A 9000lb winch will generally pull 3-400amps continuous when under full load.
The Redarc isolators are only rated at 100 or 200amps continuous dependent on model.
As it is effectively joining the batteries in parallel, the load will be equal on both batteries and full current load will have to pass through the underrated isolator , possibly resulting in a melted isolator or fire.
Agree with what you are saying but the manufacturers definitely say it is possible and recommend the use of their solenoid through winching (check the website) the only thing I can put it down to is that they massively underrate the isolators. The size of the terminals on the redarc alone suggest to me they are capable of much more than 100 amps. It is definitely worth keeping in mind and if it did self destruct there would be a warranty case for sure.